Hello trent_miller172
In TIA V20, device version V16 cannot be selected for Comfort Panels; only versions 14.0.1.0 and 17.0.0.0 are selectable. I recommend selecting version 17 for the TP700 in TIA V20. Then it is necessary to perform an OS update to image V17 on the panel.
Alternatively to ProSave (or TIA Portal), there is the option to perform an OS update via memory card. https://support.industry.siemens.com/cs/us/en/view/109740696
If you want to perform the OS update from within the TIA Portal V20 environment, the panel images must first be installed in the corresponding folder structure (TIA V20). For TIA V20, the images can be installed via the PIU (Panel Image Update). https://support.industry.siemens.com/cs/us/en/view/109825750 There is also an offline option described under point 1.2.
See the answer to 2) When there are problems installing the images in TIA V20, If the image V17 Upd8 is present on the panel, then the project can be downloaded from TIA V20 without having to perform an OS update beforehand.
Best regards, Costanza |