4/1/2022 5:53 AM | |
Joined: 8/31/2021 Last visit: 6/2/2024 Posts: 6 Rating:
Hi friends, I have the same problem F011 in my 200kw motor drive model 6SE7033-7EG69-Z. When put on 24 v supply the dc volt was showing 540V and over current trip (f011).first I checked the converter and it was fine. Then cuvc replaced from a working system but was no change. Then ct checked which was also fine.then checked power supply board and found one diode and capacitor burst so I replaced the power supply board. Still the same problem. Then replaced the IVI and try to start but the result was the same.then checked the igbt which was aldo found in good condition. Last I replaced the igbt control module card and escaped f011 and system start to run. Thanks for all the members who gave their suggetion in the same category. Regards Omana kuttan ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/01/2022 05:54:21New subject after splitting |
4/1/2022 5:55 AM | |
Joined: 6/19/2017 Last visit: 6/28/2024 Posts: 8182 Rating:
Closed cause question posted twice. The second thread with the subject Fault code F011 is published within the conference SIMOVERT MASTERDRIVES. Jen_Moderator |