Do you see any issues with this program?
AttachmentRepeating Loop with 2 limits start stop and safeties.zip (237 Downloads) |
10/6/2023 2:10 PM | |
Try this one. If both limit switches are activated at the same time (one sticks and the other is activated) then it stops. If the cylinder does not extend in the set amount of time, activating the limit switch, it stops.
AttachmentRepeating Loop with 2 limits start stop and safeties V2.zip (303 Downloads) |
10/6/2023 3:52 PM | |
Joined: 12/18/2014 Last visit: 8/15/2024 Posts: 33570 Rating:
Try this. You must chance the timer values and the number of loops to your wish. AttachmentRepeating Loop with 2 limits start stop and safeties_V2.zip (247 Downloads) |
10/9/2023 2:35 PM | |
Unless I am missing something, the maximum time for step 2 times out regardless if Limit Switch 1 is activated. |
10/9/2023 5:30 PM | |
I made a little chance, try this.
AttachmentRepeating Loop with 2 limits start stop and safeties_V3.zip (268 Downloads) |