Dear team, I'm trying to change the temperature sensor type from kty84 to pt1000 in p601. But it doesn't change with error parameter illegal value... Please suggest me why it is not changing.. Conversely, even if I'm trying to change the setting from KTY 84 to PT1000, I cannot change it. I checked https://support.industry.siemens.com/cs/ww/en/view/109483388 this webpage But I don`t know how I can download FW version V4.7 HF17. Our firmware are 4.7.0.16 and 4.7.0.29. Does it same firmware version? I mean 4.7.0.16 or 4.7.0.29 = 4.7 HF17 And What is meaning of HF in FW version V4.7 HF17. And Additionally , What is the reason that siemens temp sensor type changed KTY84 into PT1000? Regards Kim |
Last edited by: AutoGen_6386154 at: 04/05/2024 12:09:38Last edited by: AutoGen_6386154 at: 04/05/2024 21:37:27 |
|
5/8/2024 1:07 PM | |
Joined: 4/24/2008 Last visit: 8/2/2024 Posts: 213 Rating: (16) |
HF means Hotfix. x.x.0.16 is Hotfix 16, and you need at least x.x.x.17 |
|
|