11/27/2024 7:54 PM | |
Joined: 2/11/2024 Last visit: 1/24/2025 Posts: 16 Rating: (0) |
Dear experts, I have a project with TIA Portal V19 where I will use a SCALANCE XC408M-4C switch (6GK5408-4GP00-2AM2) of FW:6.3. In addition to the above, has anybody performed a FW upgrade on that switch to share any points of attention for the process? Also how much time the FW upgrade takes? Because I tried to load FW 6.6 with WBM but the progress bar stayed at 0% even after 15 minutes. Either of the above solutions is suitable for us, so your assistance will be much appreciated. Thank you in advance. |
11/29/2024 11:03 AM | |
Joined: 8/3/2009 Last visit: 1/23/2025 Posts: 14651 Rating: (1823) |
Hello ThanosMrtds Do you have tried the FW Upgrade from here: https://support.industry.siemens.com/cs/de/en/view/109955252 Bye Murof |
If this Information really helps, you could use the Rate function |
|
1/14/2025 7:50 PM | |
Joined: 2/11/2024 Last visit: 1/24/2025 Posts: 16 Rating: (0) |
Hello Murof, Thank you for your assistance! Please be informed that we managed to perform FW upgrade to latest version. We connected to the MGMT Interface and we downloaded the FW upgrade. During our previous attempts we were connected to a normal interface of the switch, so that was the reason we could not perform the upgrade. Thank you once again, and sorry for my late response. |