1/31/2021 4:07 PM | |
Posts: 5 Rating: (0) |
HI,We have the same problem as you. What did you do to solve the problem? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/02/2021 07:46:00New subject after splitting |
|
2/6/2021 6:01 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Drive part number is 6SE7024-4CC20 & not ES. Please set p060 = 3 & then try to change p071 i.e. line voltage. |
2/28/2021 11:32 AM | |
Posts: 5 Rating: (0) |
Hi petr_sipor,I did these steps according to the documents before, but I could not set the p071 parameter to 100. |
Last edited by: mhd99 at: 02/28/2021 11:35:51 |
|
2/28/2021 11:48 AM | |
Posts: 5 Rating: (0) |
Hi PISCEAN 2010 ,The p060 parameter is not available on our drive. |