3/23/2020 8:54 AM | |
Joined: 10/18/2012 Last visit: 8/21/2024 Posts: 225 Rating: (23) |
Dear Sen_I &, ensure, that the boot-device (your HDD) is ok. i.e. look into the BIOS Setup menu and verify the status of the connected hard drive. The IPC should be configured to boot from the HDD. See PDF-manual of IPC677C at chapter 16.4, page 241 here: https://support.industry.siemens.com/cs/ww/en/view/43495460. regards,
|
Last edited by: xnor at: 03/23/2020 08:57:43changed link to manual in english language |
|
3/25/2020 11:35 AM | |
Joined: 10/18/2012 Last visit: 8/21/2024 Posts: 225 Rating: (23) |
Dear Senthil, If the HDD was detected one but now the HDD is not detecting anymore - this indicates some kind of HDD failure to me. Windows recovery option will not help you until the HDD works again. In case of a HDD failure the HDD must be replaced with a new HDD. All the software including the operating system, application software and HMI projects need to be transfered to the new HDD. I can't tell you what software you need. That depends on what the IPC was used for. I hope you have some backup data from that IPC. If not, then a professional data recovery service may help you to get the data from the failed HDD. I suggest you contact a Siemens Repair Center. You find the next Repair Center in your region look at the following webpage: I wish you all the best! |
3/26/2020 9:51 AM | |
Posts: 8 Rating: (0) |
Dear Xnor, Thank you very much for all your support. Please find attached HMI project file details. Regards Senthil AttachmentHMI File extension.pdf (580 Downloads) |