4/4/2022 2:18 PM | |
Joined: 4/1/2022 Last visit: 3/4/2023 Posts: 6 Rating:
|
During the commissioning I can set PLC parameters: Attachmentattachments.zip (421 Downloads) |
4/4/2022 4:37 PM | |
Joined: 5/24/2016 Last visit: 9/11/2025 Posts: 412 Rating:
|
Hello. According to you drawing all your feedback for reference and limit switches are NO? Is this correct? I do not know if you have the manuals. But here you can download the following. SINUMERIK 808D ADVANCED Commissioning Manual In the Function manual I would like to pay your attenction to 17 - Reference point approach (R1) SINUMERIK 808D ADVANCED Function Manual |
4/4/2022 5:21 PM | |
Joined: 4/1/2022 Last visit: 3/4/2023 Posts: 6 Rating:
|
Hello. I am very sorry. I drew limit switches as NO but in fact they are NC and I have them like that. Reference switches are NO. Thank you for the second manual. I did not have that one. I will read it and hopefuly on Friday I will be able figure something out. Have a great day |
Last edited by: Jake_2148 at: 04/06/2022 22:03:18 |
|
4/4/2022 5:31 PM | |
Joined: 4/1/2022 Last visit: 3/4/2023 Posts: 6 Rating:
|
What bothers me the most is the fact that I was able to reference the Z-axis but I am not able to reference the X-axis. I checked if all parameters of axes are the same and they are actually. |