Hello, Can I send historical data on the server ? |
2/21/2023 7:45 AM | |
Joined: 4/8/2021 Last visit: 8/26/2025 Posts: 640 Rating:
|
Hi Sahil, As I said before, unfortunatelly the Comfort panels cannot be connected directly to a SQL Server. You can save the data on a USB using the DataLogs. Regarding the PLC-SQL Server connection, you can do it using a S7-1200/1500 Simatic controller: https://support.industry.siemens.com/cs/ww/en/view/109779336 Hope it helps. |
Best regards, |
|
This contribution was helpful to
1 thankful Users |
2/22/2023 1:37 PM | |
Joined: 8/3/2009 Last visit: 9/3/2025 Posts: 16322 Rating:
|
Hello Sahil_1998 Yes I can confirm that Comfort Panels cannot do a direct connection to a SQL Server (Only PC RT Systems): https://support.industry.siemens.com/cs/ww/en/view/61883659 As an alternative you can connect your Comfort Panel to a network share wo store files on a server: https://support.industry.siemens.com/cs/ww/en/view/92346478 Bye Murof |