Hi, During event analysis, we should rely on alarm message which consists of more accurate timestamp. Hence, all the digital signals and alarms should refer only the process alarm mesage. For the timestamp in trending, they normally compressed or round up to 5 seconds. For details, you need to check on the each individual tag Tag Logging settings. Normally swinging door might apply to make the archiving optimize. Search Swing door in this link. https://support.industry.siemens.com/cs/ww/en/view/109760739 In short, please refer to alarm message timestamp instead of trending timestamp. Hope it helps. |