Time Zone in HMI must be equal to Time Zone in PLC, Be sure to configure both |
This contribution was helpful to
1 thankful Users |
11/23/2024 2:10 PM | |
Joined: 11/23/2024 Last visit: 11/23/2024 Posts: 1 Rating:
|
I had the same problem. Check if you have the option " Full access (no protection)" enabled on the PLC. Another option is to disable the option " secure HMI communication". I hope this helped you. There are pictures in the ZIP file to make it easier to find the options.