I found this when I compiled. It's written So what should I do? should I erase the module? |
11/24/2024 9:47 AM | |
Joined: 1/21/2013 Last visit: 9/11/2025 Posts: 4102 Rating:
|
Hi hirorama, The problem is therefore caused by the interface module. You are using the SIMATIC ET 200SP, PROFINET interface module IM 155-6PN Basic, which has a very limited range of functions. In your case, the maximum address space of 32 bytes is the limiting factor. Since each SIMATIC ET 200SP analogue input module AI 8xI 2-/4-wire BA occupies 16 bytes of address space, you are limited to 2 such modules. Assuming that the analogue inputs are required, the cheapest modification would be to replace the interface module. The SIMATIC ET 200SP, PROFINET interface module IM 155-6 PN ST provides 1440 bytes of address space. This is more than you need. Kind regards |
This contribution was helpful to
1 thankful Users |