12/4/2024 10:44 AM | |
Joined: 2/15/2019 Last visit: 12/4/2024 Posts: 3 Rating:
|
Hello Cristoper i have s7300 with CU3202DP v4.8, I try it with simatic manager it is working fine communication ok and recieve telegram. but when i try with TIA portal the drives not recieve and sent telegram. i created same logic on both but it is not working tia portal kindly reply ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 12/04/2024 11:33:23New subject after splitting Shahzaib Khan |
|
12/4/2024 4:17 PM | |
Joined: 7/7/2010 Last visit: 9/5/2025 Posts: 16061 Rating:
|
Are both the VFD and s7-300 PLC in the same TIA Portal project? Are you migrating a classic step 7 project to TIA Portal? Have you downloaded the PLC project to the s7-300 PLC? In the portal project, is the VFD connected in the devices and networks pane and the s7-300 configured as the PN master controller? Screenshots of the hardware configuration for devices/networks in portal would be useful. Are you using startdrive? Do you have the latest V16 update installed? What firmware is installed in the CU320-2PN?
|
science guy |
|