Hi Luh_Days, 1- Have you assigned the periphery to a PLC? 2- Please install the HSP for V19 and configure the ET200SP by catalog instead of GSD and try to solve your problem: 3- Check that you are following the correct procedure: Assigning a PROFIsafe address of the F-I/Os with SIMATIC Safety |
If this information really helps, you could use the Rate function. |
|
This contribution was helpful to
1 thankful Users |
1/21/2025 10:29 AM | |
Joined: 7/9/2015 Last visit: 8/29/2025 Posts: 4443 Rating:
|
Hi, you projected ET200SP with GSD - for this you need FCT for F-Adress assignment. SIMATIC S7-Fail-safe Configuration Tool (S7-FCT)Regards, Towome |
|
|