11/28/2012 2:40 PM | |
Joined: 9/27/2006 Last visit: 9/9/2025 Posts: 12401 Rating:
|
Hello Kiren; The S7-400 CPUs will tell you in "plain" language what issues they have through the diagnostic buffer, but that does require Step 7 and a programming console at site (and someone whoi knows how to yuse them). The CPUs also use the diagnostic LEDs on the front of the modules to indicate the general area of the problem. Diagnostic LEDs of the S7-400 CPUsand their interpretation are descibed here, in chapter 2: SIMATIC S7-400 S7-400 Automation System, CPU Specifications If you have a BATF LED active I can only suggest you change the present batteries in yous power supply module (without removing power to the CPU, this would erase the RAM memory). The procedure is described in the Hardware manual of the S7-400, chapters 7.1 (and 6.8 if the batteries need depassivation): Automation System S7-400 Hardware and Installation Hope this helps, Daniel Chartier |
12/18/2012 11:45 AM | |
Posts: 33 Rating:
|
Dear ALL, I am on site now and i could see that while in stop mode CPU shows INTF (internal fault)...I thought either CPU or program !! So, i was thinking that anyway CPU must be OK as this problem comes once in 2 days...So, I have downloadedfresh program (Back up)..and kept in observation...Now next time again in 2-3 days , i fi don't see this problem again then problem was with program only.. I have attched the screens shots of diagnosis (lot many shots)..Please advise if you can guide me little after looking at scree shots...Even in diagnosis, it shows that issues was with some FC 854 and OB21..So, i thought it can be issue with Program only.. Regards Kiren Attachmenthardwrae diagnostci buffer.pdf (878 Downloads) |
12/18/2012 12:06 PM | |
Posts: 1064 Rating:
|
item number 3 in your log is showing a area lenght fault in the called db which is putting you in stop mode |
Follow us on