Dear experts, I wanted to show diagnostics buffer on Wincc V7.3, I am so confused from the posts found from this forum.. Please suggest the solution.... ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/17/2019 11:48:37New subject after splitting |
|
| 10/29/2019 5:03 PM | |
|
Posts: 821 Rating:
|
Hi, this might help you: https://support.industry.siemens.com/cs/mx/en/view/109757865 B.R. |
| 10/29/2019 6:38 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello Ajay; I am afraid that Healthcheck's proposed link discusses WinCC diagnostics, which is not what you are asking about, if I understood your request correctly. If what you want is the contents of the PLC diagnostic buffer appearing in your WinCC project, the closest you can get to that result with WinCC v7.x uses the Report System Errors function in the PLC configuration to generate messages that are linked to different diagnostic OBs: list distributed I/O station, OB 86; programming error, OB 122.. These messages can then be read in the WinCC runtime alarms and messages. Have a look at the following step-by-step instructions for Reprt System Error messaging, and pay attention to the prerequisites: WinCC must be integrated in the Step 7 project, you must use AS-OS engineering... https://support.industry.siemens.com/cs/ww/en/view/22727527 Hope this helps, |
| 9/21/2021 11:18 AM | |
|
Posts: 9 Rating:
|
PLC: S7-1516 3 PN/DP Tia portal v13 WinCC v7.3 I want to show diagnostic buffer on my SCADA (winCC v7.3) of PLC. Please suggest some methods?? |