(1)| 2/10/2022 4:19 PM | |
|
Posts: 6 Rating:
|
Hi, thank you very much. It fixed my problem with the colors. But now I have a problem with my connection to the PLC's. I checked it and as soon as I made the update for the winCC the connection cannot be established anymore. To ping the PLC's is no problem Do you know maybe what the issue could be? I'm using S7-1500 Channel OMS+ My PLC's are 1518F-4 with Firmware version v2.9 Siamtic Net 16 is installed ------------------------------------------------------------------------------------------ |
Last edited by: roxas21 at: 02/10/2022 16:49:11Last edited by: Jen_Moderator at: 02/11/2022 09:57:27New subject after splitting |
|
| 2/11/2022 8:37 AM | |
|
Joined: 8/3/2009 Last visit: 1/9/2026 Posts: 16629 Rating:
|
Hello roxas21 I know the reason it is all about the new security features of the enchrypted HMI connection. you have to do exactly all steps of this FAQ (also if you have disabled the secure HMI conneciton in the PLC): https://support.industry.siemens.com/cs/de/en/view/109798498 Because of the Upd 4 or newer you only can work with the new 2.9 FW together with importing the certificate like in the FAQ described. Bye Murof |
|
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
|
|
| 2/15/2022 4:29 PM | |
|
Posts: 6 Rating:
|
Hallo Murof, that solved my problem. Thank you very much! |