hi Matthias, Profibus GSD file can be found here: Download GSD File CM 1242-5The operation manual of the module can be found here: Operating Instructions CM 1242-5When projecting this module you need to set transfer areas, which are the IOs from this slave. What it output on your side is input on the master. and this needs to suit the slots. So when you have 10 bytes input on the CM1242-5, the master needs to have 10 Bytes Output on the first slot. hope this helps, regards, |
This contribution was helpful to
|
|
| 2/18/2022 2:56 PM | |
|
Joined: 3/11/2019 Last visit: 1/7/2026 Posts: 1653 Rating:
|
Hi MatthiasG, as i understand, the CPU-1200 with CM should work as an I-Slave with a seperate master. Therefore, following FAQ may be helpful. Indeed, there is another hardware used, but the basic function/principle is the same. How to you connect the communication module CM 1542-5 or the communications processor CP 1542-5 as I slave in STEP 7 V5.x to an S7-300/S7-400 CPU?maybe this helps regards sancruz |
|