(1)| 7/18/2022 4:39 PM | |
|
Joined: 1/21/2016 Last visit: 2/7/2025 Posts: 88 Rating:
|
Hello I have the same problem, impossible to assign the profisafe address on a safety input module. The module whose address I am trying to assign comes from another installation, it was paired with a 1516TF CPU. For the sake of supplying safety cards, we took this card for a new installation with a CPU 1510SP F. But I feel like that's a problem. Does anyone have a solution, CPU: 6ES7 510-1SJ01-0AB0 Safety Card: 6ES7 136-6BA00-0CA0 Cordially. ------------------------------------------------------------------------------------------ |
Last edited by: ERPA_France at: 07/18/2022 16:45:18Last edited by: ERPA_France at: 07/18/2022 17:22:55Last edited by: Jen_Moderator at: 07/19/2022 08:07:32New subject after splitting Cordially, |
|
| 7/19/2022 7:29 AM | |
|
Joined: 1/21/2013 Last visit: 1/21/2026 Posts: 4424 Rating:
|
Hi ERPA_France, did you only use the F-DI module from the other installation, or also the base unit? You will need the electronic coding element that is in the base unit after it has been plugged in for the first time. See "What should you check when the F destination addresses cannot be assigned?". Kind regards |