Hello , I have 02 WinCC servers Engineering : 192.168.45.xx Runtime: 192.168.11.xx Firewall port openned: 102,1033,2308,5001,5002,50523,4840,4861,135 Please support me guide how to configures for can show IP runtime on Simatic shell of engineering Thanks! ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 10/28/2022 12:08:59New subject after splitting |
|
| 11/4/2022 10:16 AM | |
|
Joined: 8/3/2009 Last visit: 1/30/2026 Posts: 16680 Rating:
|
Hello Dung922 the Simatic Shell communication works only in the same subnet by default. But you can use one station of each subnet as Multicast Proxy in the Simatic Net terminaladapter settings. If there is a firewall between you should also use an enchrypted communication with a defined port (also in Simatic Shell Settings). Of course you have to reach the other station via ethernet (Ping OK?) Check this FAQ here you should find also all information: https://support.industry.siemens.com/cs/de/en/view/109771695
Bye Murof |
|