Hello DIKE, You already received answer from gumis how to make communication between CPU and Simoreg via Profibus. When you make settings in hardware configuration with adding of GSD file for Simoreg, you could choice between different type (different numbers of words that will exchange data between PLC and Simoreg). Set PPO type 5. In your case needs to receiving Ia actual current. This should be set first in Drive Monitor - paremeter P734.3 or 4 or...=K117. And let's say addresses in hardware configuration are start from 256. So in Step7 (easiest way) use L and T functions. For example Load the third word (260) and transfer to some MW... I suggest you to look at drive's manual - SIMOREG DC Master 6RA70; software version 3.1 . Then here you could find some examples about communication between drive and PLC. (Sorry not the same type like yours but the way (the style) is the same). Hope this will helps. Best regards Hristo Mihalev |
5/9/2009 3:19 PM | |
Posts: 3 Rating: (0) |
Thanking you, Herewith i enclosed my simoreg parameter for your information.U 734 assign for profibus connection. Now i think about all parameter list and i need time for further discussion. I want to know FC 21,FC 22,FC 23 function block in PLC how it helps in PLC program for send and receive information from simoreg. Attachmentwtrt.pdf (812 Downloads) |