Hello Mr. I have 1 problem. Our SERVER computer is down. Now we don't know what CLient does when connecting PCs to CPUs. That is, we are thinking how to use Clinet computers without Server computers. Can you advise on this? I will send you the connection diagram. Thanks in advance for your advice. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/01/2023 11:45:41New subject after splitting |
|
| 3/2/2023 12:36 AM | |
|
Joined: 9/9/2015 Last visit: 12/5/2025 Posts: 732 Rating:
|
Hi, I believe server is the stations that have direct connection to plant bus (PLC network). Hence, it is not possible to have monitoring and control without server station up. However, you can achieve it my reconfigure the project, install network adapter in your client station, move licenses to client and move the plant bus connections to client network. I can learn more in https://support.industry.siemens.com/cs/sg/en/view/109801081 |
|
Please give me 5 stars Rating if my post is helpful for you. :) |
|