Hello, look to my previous post where I describe cleary where you need pay attention - CP341 Master/Slave driver problematic. I see your problem here, with no correct blocks used as is described in my mentioned documentations. You need use P_SND_RK and P_RCV_RK blocks and need configure cfg block correctly with parameters as you need. This system of cfg is little bit different to your mentioned system blocks for MB RTU functionality. Here is recommended documentation what can help you: S7-300/400 Loadable driver MB RTU Master Sry, what I see now from your screenshot as block cfg. This is not relevant as topic problematic but only as tip for you generally. What is reason to cut EN input of block? Generally this is not recommended only in case you know what you do, simply is recommended to have this input without any condition. For block handling, you have there other important input parameters. Important cfg on CP341 HW module: in case of use Master functionality, you need set this option under Protocol option field. |