Hello Engr@IND Basically if the HMI is not set as IO device then you will not have to put the HMI in HW config and also you do not have to program something in the PLC. The HMI connects in runtime dynamically. If you want to use interated functions or symbolic addressing in HMI project then you have to use an integrated communication connection in the same TIA project or by the use of Proxy Device. If you use a manual HMi connection then you can also address absolute (if you use non optimized DBs). Also older S7300 communcation can be done then you have to activate PutGetcommunication in security settings. here are some basic information about creating HMI communication connection: https://support.industry.siemens.com/cs/de/en/view/89852595 Bye Murof |
|