Same with me. It's now January 2023 :( |
1/28/2023 1:52 PM | |
Joined: 8/31/2010 Last visit: 7/18/2025 Posts: 1525 Rating:
|
Hello Users, I used WinCC Unified V18 here. (configured MTP1000 in it and used simulation) I also observed the similar behavior as mentioned above by you all. Look for "Alarms - show current" in this Alarm Control section of WinCC Unified Engineering V18 - System Manual. By pressing the "Alarms - show current" button, you can scroll the active alarms. However by default this button is not pressed. Check this out and share your experience. |
Last edited by: Ganes10 at: 01/28/2023 20:14:13Like it? Rate it! |
|
This contribution was helpful to
2 thankful Users |
4/27/2023 7:03 AM | |
Joined: 9/19/2022 Last visit: 8/12/2025 Posts: 4 Rating:
|
Hi, I've been testing some configurations for the Alarm control. If you want to be able to scroll the alarms straight without using the button on the function bar, you have to go the alarm control properties. If you uncheck this option, when you open the alarm control you will be able to scroll without using any button. You can also choose if you want the last alarm to appear on top or bottom on the format properties. Properties -> Format -> Sorting direction -> Ascending or descending You can also use the filter if you want to show only the active alarms, by checking State = Incoming. Hope this can help any of you. |
This contribution was helpful to
28 thankful Users
|