(0)| 4/26/2023 4:46 PM | |
|
Posts: 1 Rating:
|
Please would you give me more details about your configuration? I've managed to establish communication between a s7-1500 and 16 Danfoss FC 302 with Eth/IP Option. However, the delay is too much, up to10 seconds in some cases. I am trying to change my cyclic OB Time (10 ms) or the RPI (I've tried with 10, 30, 50 ms) of the drivers without any important change. This delay activates alarms and warnings in the drivers. I am looking for some advice. ------------------------------------------------------------------------------------------ |