(0)| 7/3/2023 2:54 PM | |
|
Joined: 10/22/2011 Last visit: 12/6/2025 Posts: 309 Rating:
|
Hello All, I am trying to restore a backup file of KTP700 Basic DP into the same type of panel but there is no communication between HMI and Prosave I am using PC Adapter USB. it is a new HMI If I make a new program in TIA portal and download it then it is successful But when I try to communicate it with prosave then no communication Please suggest solution
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/04/2023 08:08:40New subject after splitting |
|
| 7/10/2023 11:56 AM | |
|
Joined: 8/3/2009 Last visit: 1/16/2026 Posts: 16644 Rating:
|
Hello Shebi87 This Adapter is not released with this kind of panel: https://support.industry.siemens.com/cs/de/en/view/19109408
I would recommend using communication processor like a CP5711 bye Murof |
|
If this Information really helps, you could use the Rate function |
|