Hello, How can configurate PN/PN Coupler in PCS7 to can communicate with other controller (no siemens controller)? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/02/2023 09:50:32New subject after splitting |
|
| 3/2/2023 9:04 AM | |
|
Joined: 3/11/2019 Last visit: 1/7/2026 Posts: 1653 Rating:
|
Hi lazarvlad,
Unfortunately, I am not sure how this work with PCS7, or the configuration process is different at all. But there is an FAQ available and there are also some statements according PN/PN coupler. Maybte this can help somehow. What options does SIMATIC PCS 7 offer for integrating third-party automation?regards sancruz |
|
Feedback appreciated, please rate |
|
| 3/2/2023 11:59 AM | |
|
Joined: 10/26/2011 Last visit: 1/13/2026 Posts: 766 Rating:
|
Hello Iazarvlad, in the following application example a step by step instruction describes in detail the configuration of the PN/PN coupler: Redundant Process Data Transfer with the SIMATIC PN/PN Coupler and SIMATIC PCS 7 |
|