Hi RUTURAJSINGH, It is a licensing problem since your license allows you up to a maximum of 4096 variables that you can communicate with your PLC. If you exceed this limit, as in your case, you are exchanging 5561 variables, you will be exceeding this limit. There are licenses available to extend the powertags. In the following link, in the 'Ordering data' section you can find the excel (also attached) with all the available licenses: "Delivery release SIMATIC WinCC V17" If you do not know which one you need, let me know and I will tell you which one you should purchase. Best regards! AttachmentWinCC_V17_MLFB_list (1).xlsx (489 Downloads) |
|
If this Information really helps, you could use the Rate function |
|
| 4/24/2023 10:56 AM | |
|
Joined: 8/3/2009 Last visit: 1/23/2026 Posts: 16661 Rating:
|
Hello RUTURAJSINGH Yes you need a bigger license but This will not a reason for performance issues. A bigger license will no increase your speed and performance. Check out also this FAQ for Information: https://support.industry.siemens.com/cs/ww/en/view/109479986 Bye Murof |
|