Hi, It looks like you have SELFRESET set to 1. After Completed, the SFC will reset itself to Idle. Completed signal is given, but it's only a pulse for the duration of the OB the SFC runs in. If you set SELFRESET to 0, the SFC remains in Completed state until you set Reset to 1 (in automatic mode). |
|
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
|
|
| 8/14/2023 4:55 AM | |
|
Joined: 3/14/2008 Last visit: 1/19/2026 Posts: 2233 Rating:
|
Hi, A new START trigger will also work yes |
|
If I could help you, you can use the RATE button. Thank you. |
|
| 8/14/2023 6:34 AM | |
|
Posts: 8 Rating:
|
The solution worked. Thanks! |