Hi everybody, I have problem with Modbus RTU communication. Error No. 8180 is appearing in block MB_COMM_LOAD at startup and then in MB_MASTER block. According to me, the MB_COMM_LOAD block doesn't finish at all. I'm using 1212C with communication module CB1241. I have read many posts but I have not been able to solve the problem. My target is Modbus communication between PLC(master) and four arduinos (slaves). I'm using ArduinoModbus library and it works correctly. I would like start blink the LED on one arduino when i push the button at input I0.0 in PLC. Can you help me, please? Does anyone see, where can be a problem? I attached prints to the pdf. Thank you very much. BR Jenda AttachmentMBCOM.pdf (696 Downloads) |
| 11/14/2022 3:15 PM | |
|
Joined: 8/12/2021 Last visit: 1/15/2026 Posts: 351 Rating:
|
Hi _Jenda_! It seems that error 8180 in Comm_Load is not categorised. However, this code is available in the Master function. |
|
If this Information really helps, you could use the Rate function |
|
| 10/30/2023 3:33 PM | |
|
Posts: 1 Rating:
|
Awsome!!! It worked. Thank you!! |