(0)| 11/1/2017 4:39 PM | |
|
Joined: 2/16/2010 Last visit: 8/8/2025 Posts: 5 Rating:
|
Hi, do you have any success with Bently Nevada? I tried today establish Modbus TCP connection with my S7-1516 but without success. I have connected BN card 3500/92 to CPU port X2 via Scalance X208. Port X1 is use for Profinet ring. CPU IP is 192.168.1.2 and BN IP is 192.168.1.6. I can ping BN so card should be available. Settings of BN are attached. Settings of SW and results are also attached. Result what I get is still the same - error with status value 809B. I tried set Modbus Server and also Modbus Client but no change. Please help if you know how to fix it. Thank you. RomanST ------------------------------------------------------------------------------------------ AttachmentModbus.zip (770 Downloads) |
Last edited by: Jen_Moderator at: 11/3/2017 12:11:12 PMNew subject after splitting |
|
| 11/3/2017 12:34 PM | |
|
Joined: 4/28/2015 Last visit: 11/27/2025 Posts: 10970 Rating:
|
Hello, which local/remote port value? |
|
With best regards... |
|
| 11/11/2017 11:55 PM | |
|
Joined: 2/16/2010 Last visit: 8/8/2025 Posts: 5 Rating:
|
Hello, Modbus connection is working. MB_Client used for S7-1516, Bently Nevada is Modbus Server. Interface ID = 72 - PLC CPU ethernet port hardware ID where Modbus is connected ID = 1 - any unique number ConnectionType = 11 - TCP/IP connection ActiveEstablished = TRUE RemoteAddress = 192.168.1.6 - IP of Modbus card 3500/92 RemotePort = 502 - Port dedicated for Modbus Local port = 0 request = TRUE - permanet 1 modbusMode = 0 - any other settings doesnt work modbusDataAddress = 45001 - Modbus start address modbusDataLen = 95 - must be exactly same number as is set in BN AttachmentModbus.zip (835 Downloads) |