Hello, Looking forward to insights from the community! AttachmentUpdate time for process images.pdf (231 Downloads) |
Last edited by: ZHK at: 11/25/2024 10:38:05Last edited by: Moderator_Lan at: 11/25/2024 12:20:48link optimized |
|
| 11/27/2024 12:48 AM | |
|
Joined: 10/7/2005 Last visit: 1/16/2026 Posts: 3054 Rating:
|
That is indeed observed correctly
Be it OB1 process image or OBxx process image partition, these are internal memory areas that are simply updated with the most recent values prior to the OB call. In other words and as per FAQ 18325417 "The contents of the process image (PII and PIQ) do not reflect the actual values of the inputs/outputs, but the values at the time the process image was updated". As such, the PROFIBUS Network speed does not matter and the values on the Network may in fact change multiple times in between Process Image (partition) updates. |
|