(2)| 2/6/2020 10:14 PM | |
|
Joined: 12/13/2011 Last visit: 5/20/2025 Posts: 123 Rating:
|
I have attached a screenshot of the error in Chrome. |
| 2/7/2020 12:03 PM | |
|
Joined: 9/23/2005 Last visit: 1/19/2026 Posts: 4449 Rating:
|
Hi, If IIS was right setting, the localhost should show something. It doesn't seems to be a WinCC problem but else a Windows setup questions. Is the IIS rightly active (see https://support.industry.siemens.com/cs/ww/en/view/109773589 )? Which browser do you use (see https://support.industry.siemens.com/cs/ww/en/view/109757952)?
Did you tried to type the computer name as address? |
|
Denilson Pegaia |
|
This contribution was helpful to
|
|
| 5/9/2024 6:30 AM | |
|
Joined: 6/14/2011 Last visit: 12/17/2025 Posts: 3 Rating:
|
I am using TIA V19 and WinCC unified, facing issue of WebRH page is not reachable with https://localhost/WebRH However I can connect with https://ipaddress/WebRH , but facing issue of Swaclogin is unavailable error. SOLVED: Both issues are resolved by switch off/disable the proxy server. ( In Windows 11 OS -> Network & Internet > Manual proxy setup > Under Edit proxy server switch off proxy server.) Refer attachment for error details and proxy server settings. AttachmentProxy server setting.zip (615 Downloads) |