Hi, I believe only versions >= 4.0 of the Modbus TCP library use TCON_IP_V4 and TCON_Configured system data types at the CONNECT input parameter. This is stated here: Differences between the versions <= V3.x and >= V4.0 of the Modbus TCP library If you follow this documentation MB_SERVER: Communicating via PROFINET as a Modbus TCP server and the error persists, then please perform the error logic in the communication block that has the error, based on this FAQ: How do you evaluate the status of system blocks in STEP 7 (TIA Portal)? That is, when the 'ERROR' parameter of the communication block is set to '1', use the MOVE block to move the value of the 'STATUS' parameter of the block to an auxiliary tag. What is the value of this tag? |