Hello AutoGen_3ed79 The range of upgrades is divided into:
PCS 7 does not support a direct upgrade from V7.0 to V10.0 SP1. You’ll need to perform intermediate upgrades from PCS 7 V7.x to V8.2, then to V9.x, and follow the guidelines in the manual "Process Control System PCS 7 – Software Update with Utilization of New Functions V9.1" to transition to V9.1 before finally upgrading to V10.0 SP1. Hope this helps! |