7/22/2025 9:49 AM | |
Joined: 5/21/2013 Last visit: 9/2/2025 Posts: 28 Rating:
|
Hi Experts What could be the cause of 2 or more interlock *first signals* displaying simultaneously. |
7/22/2025 1:39 PM | |
Joined: 2/1/2010 Last visit: 9/3/2025 Posts: 212 Rating:
|
Yes it is possible this can happen if the input conditions change state on multiple interlock inputs on exactly the same scan. Examples of how this happens: 1. if you have connected both inputs to the same exact source (this is the easiest way to reproduce it for demonstration purposes) 2. having unique/divergent logic that happened exactly simultaneously. I think its a quite rare event in real time. (unless you have logic that makes both input conditions happen at the same time due to code scan order originating from a common initiating event, then maybe it always happens. In this case you may want to evaluate your ILK conditions further) |
Last edited by: RVS.wick at: 07/22/2025 13:40:20If my post helped you, please rate. Thanks. |
|
8/27/2025 1:08 PM | |
Joined: 5/21/2013 Last visit: 9/2/2025 Posts: 28 Rating:
|
Thank you |