Hi automation_1, The attached doc has the information about SFC 58 and 59. As Aret told, with the S7-400, the SFCs 55 to 59 can also return the error information W#16#80Fx. In this case an error occurred that could not be localized. Regards ddg AttachmentSFC_e.pdf (439 Downloads) |
This contribution was helpful to
|
|
| 7/14/2009 9:29 AM | |
|
Posts: 133 Rating:
|
thank you for the answer, i.m sorry buti don` tunderstand where sfc58/59 put data sent/received; |
| 7/14/2009 10:41 AM | |
|
Posts: 535 Rating:
|
Dear automation_1, you have to define the buffer using an ANY-Pointer at the RECORD-Parameter (e.g. P#DB11.DBX10.0 BYTE 10). Have a look at this link, where the usage of ANY-pointer is described. Regards, yy1 |