(0)| 5/11/2009 4:26 PM | |
|
Posts: 406 Rating:
|
Hi... Thanks for your reply....... I also attach themodule informationmsg......... I again download the driver but it is showing "driver already exists" msg....... Still SF is showing what may be the problem... Helpme out from this issue.... Attachmentdiagnostic.zip (300 Downloads) |
| 5/12/2009 7:46 AM | |
|
Joined: 3/21/2006 Last visit: 1/10/2026 Posts: 10247 Rating:
|
Hello samkcr, Basicly SF led is on in the beginning after apply line voltage to the power supply module. When the initialization phase completes, the SF LED on the CP 341 is on. (Before assigning parameters for the CP 341). And you receive the same error in diagnostic buffer.("Parameters have not been assigned to the module"). I suggest you to look at CP 341 - First Steps in Commissioning manual and start again with parameters. If you receive the same error again after that, might be the module is defected. If you have anothger one - change it and try... Hope this will helps. Best regards Hristo Mihalev |
| 8/27/2009 3:37 PM | |
|
Posts: 34 Rating:
|
Hello Samkcr, I had a quite similar problem with 341 y H system, but we used modbus RTU. The problem was solved wit this FAQ http://support.automation.siemens.com/WW/view/en/17854293 I saw in the screenshots that you have an error in PLC, is that error involved in the 341 error? Hope this helps Kind regards |