10/10/2009 2:13 PM | |
Posts: 212 Rating:
|
Dear DesignTech, You need to create a configured connection between AS and OS in Netpro and need to activate check box :: Activate Maximum Redundancy. This will allow you to use 2 CP 443-1 and 2 CP 1613 to its maximum possible way. Also you need to have proper design of the scalance to achive redundancy to full level. Same is explained by me in link below. https://www.automation.siemens.com/IN/tf/WW/en/Posts/33797#top |
Last edited by: ABN at: 10/10/2009 2:15 PM |
|