hi, Wincc Flexible 2008 Advanced |
| 2/2/2010 12:53 PM | |
|
Posts: 5 Rating:
|
hi am using Simatic Multi Panel 377 15inches |
| 2/3/2010 2:00 PM | |
|
Posts: 836 Rating:
|
Hi Jeevamv, the MP377 is limited by the max. quantity of scripts. If you exceed the limitation of 100 scripts, you will get a warning message by compiling the project. There is no way to extend this limitation with additional memory. How do you dynamize objects in WinCC flexible via scripts shows this FAQ: http://support.automation.siemens.com/WW/view/en/24249449 |
| 2/4/2010 5:34 AM | |
|
Posts: 5 Rating:
|
Dear the body, Thanks for ur Reply |