Dear all, I've download program at here. I try it in WinCC Flex 2005 and 2008 its work. but when I try it in WinCC Flex 2007, Its won't work. Why I said its won't work?? because when I set time value 100 sec in HMI it should be 100 Sec in PLC too but what I saw is 100mS(miliSecond). I try to reinstall my WinCC Flex 2007 but nothing change. The linear scaling is still not work. Any suggestions? Thank you all, |
3/8/2010 9:25 AM | |
Joined: 4/24/2006 Last visit: 9/15/2025 Posts: 9027 Rating:
|
Hi, It is a known problem of WinCC flexible 2007 There is a problem of linear scaling of S5time. You need at least Hotfix 1 to fix it. Here you can download latest hotfix for WinCC flexible 2007: hotfix 4 for WinCC flexible 2007 Best regards, Wizard |
Last edited by: Wizard at: 3/8/2010 9:28 AMSome typing errors corrected |
|
This contribution was helpful to
2 thankful Users |