Wulfgar, The best way is to use Cross Reference to check all your outputs. You can find Cross Reference under Simatic Manager->Options->Reference Data->Display By filtering the outputs, you should have only one instance of each output with W (Write). Regards, Behnam www.sigmaprocess.ca/blog |