(0)| 8/13/2010 2:27 PM | |
|
Posts: 317 Rating:
|
Hi, I think it would be better to have a standard screen with the tags of your load cell and use a multiplex tax in WinCC Flex to display the values of each cell as required. This faq shows how to use multiplex tags. http://support.automation.siemens.com/WW/view/en/21808320 |
| 8/13/2010 3:46 PM | |
|
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating:
|
Zeroptr, You have 28 Load Cells. 1.You better have 28 DBs (one for each load cell) which keep the scale values and analog values. This way you will have a clean code and know where to look for data related to each one. 2. Let's say DB1 is for Load Cell 1. "DB1.DBD0" has the output weight. 2. You need an index. Let's call it "Analog _Index". 3.You are saving the "Analog_Index" in "DB100.DBW0". 4. You setup atag in Wincc Flex. Analog_Index Word DB100.DBW0 4. You setup another tag for displaying the AnalogValues on the screen. Analog_Display Real DB [Analog_Index] DBD0 5.By changing the "Analog_Index" through HMI, you can display the output. Regards, Behnam www.sigmaprocess.ca/blog |
| 8/15/2010 5:50 PM | |
|
Posts: 31 Rating:
|
Hi All, I solved the problem with Darius way.. (He was the first answerer) I like the multiplexing the tag it's very nice.. I plan to use it at my further projects.. [schnippschnapp] New question is transferred to Does any one know the tag limit of MP277 10" Key?. |
Last edited by: O_Moderator at: 8/16/2010 8:49 AM |
|