Hi, you can find additional information here http://support.automation.siemens.com/WW/view/en/43705659 Also, follow the link at the bottom of that FAQ for extra guidance. Unless your process is really complicated, then I would strongly recommend recommissioning. Getting a CUVC to run from a digital input and follow an analog for example takes literally minutes to commission, modifyinga CU1 parameter set to load into a CUVC can take days. You need to weigh up how involved the CU1 is: for example do you have a T100 technology card attached, is there an encoder and will it need to be re-terminated is there serial or Profibus comms. These add complications, but it may still be quicker just to re-commission the CUVC from scratch. Cheers, Graeme |
9/2/2010 2:13 PM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Hello, There you'll find description for commissioning new drive - SIMOVERT MASTERDRIVES Vector Control Compendium VC34 (Operating Instructions) Best regards, Hristo Mihalev |