6SE6420-2UC13-7AA0 = MICROMASTER 420 1/3AC200-240V +10/-10% 47-63HZ F0060 = missing 24V do you have 220V? = broken fuse, incorrect line connection ….. did you install the power supply properly? = Line to L1/L; N to L2/N see attachment Attachment420_OPI_24523400_en_1006.pdf (486 Downloads) |
10/8/2010 3:19 PM | |
Posts: 739 Rating:
|
Hello , here are some more possibilities: (FAQ: http://support.automation.siemens.com/WW/view/en/8822493) A0503 = alarm, undervoltage The line supply voltage of the drive inverter is switched-out and the DP module(PROFIBUS module) is supplied through an external 24V. In this particular case, alarm message A0503 is output. This alarm message can be ignored. Normally, the electronics power supply is realized from the DC link of the driveinverter. The power supply is also sensed/measured via the DC link. When the drive inverter is powered-down, the electronics is supplied from theexternal 24V and the DC link is in a no-voltage condition. This is why A0503 isoutput. F0003 = undervoltage & F0060 = Asic time slice overflow The drive runs, the DP module (PROFIBUS module) is supplied via an external 24V supply,and the line supply (200 to 600 V AC) is disconnected. In this case, the drive is tripped with fault message F0003. |