Hi Coburger, Let´s search from forum. /tf/WW/en/Posts/44197 regards Heksu |
| 3/24/2011 3:52 PM | |
|
Posts: 180 Rating:
|
Hi Coburger, I think it´s like fault history. Look pages 44-45. F0003 Undervoltage Check the following: 1. Supply voltage (P0210) must lie within limits indicated on rating plate 2. Supply must not be susceptible to temporary failures or voltage reductions And the F0041 Stator resistance measurement failure. 1. Check if the motor is connected to the inverter 2. Check that the motor data has been entered correctly Heksu Attachmentf123.pdf (347 Downloads) |