Dear all this thread has taken on a life of its own (a week has gone and no feedback at all fromthe thread starter concerning this), so allow me to add a few morethings to be aware of in the hope it may either help ahsan1820orsomeone else who stumbles across this in the future: 1.) The obvious one: Ladder logic is the best choice to reproduce any hardwired relay based "logic" in a PLC program (this is the reason Ladder logic was invented which stronglyresembleselectrical schematics). 2.)The NOT so obvious one: A hardwiredcircuit (includingrelays, timer relays, mechancial drum sequencerns, analogue controllersetc) has its own timing rules. A direct conversion ofthese circuit toa Ladder logicbased "softwired"PLC program changes this, sinceyou are now dealing with a digital control system and its timing rules (e.g. scan based/cyclic execution). This may (or maynot) create a slightly diferent and/or non-functioning control behaviourand is at least something to be aware of and to be considered when doing the conversion. I hope this helps |
Last edited by: fritz at: 6/14/2011 3:40 AMtypos and grammar Cheers |
|