Hello Hippo_77, Already mentioned, that you will need another MP370 or the source to change it to MP377 The CP342-5 is to be used with Profibus, so you can not use it with MPI Perhaps you can use repeater to extend the length of MPI network. What should you watch out for when using the RS485 repeater in PROFIBUS and MPI bus systems? Best regards, Wizard |
| 8/5/2011 9:56 AM | |
|
Joined: 9/10/2010 Last visit: 1/6/2026 Posts: 7 Rating:
|
Thank you for your answer!. 1. Yes, I agree, that I need MP370 to make copy of existing panel. 2. Why i need CP342-5? Because existing MP370 is connected to MPI interface of CPU, I can not connect copy of MP370 to same network. New panel and old panel have same address in MPI network! And as i understand, i can not change this address even in MP370 configuration, because when project in panel is started, itis used network address of that project. So, i need other network MPI with this PLC. Yes, i know, that CP342-5 is Profibus module, but it used MPI interface as backplane connection. In STEP 7 hardware configuration you can choose address of CP342-5 in Profubus network (e.g. 2), and simultaneously, choose another address for same module in MPI network (e.g.3). So, one module can beused in 2 networks (1 electrical wiring) simultaneously, as i understand. Or am I wrong? Best regards, Hippo |