(0)| 9/5/2011 11:06 AM | |
|
Joined: 9/5/2011 Last visit: 8/18/2023 Posts: 15 Rating:
|
Dear all, Iupload my wiring method for connecting two sensor to AI SM331-1KF0A-0BA0 in pdf format . also my Pressure Transmitter have HART is it important? and what is remedy ? Attachmentdrw.pdf (409 Downloads) |
| 9/5/2011 12:56 PM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Did you connect the M- to ground too? Hart must not be a problem. Attached the manual of this (older) module. Regards, Marcjan Attachment1kf01.pdf (383 Downloads) |
|
Problem solved? |
|
| 9/16/2011 2:37 PM | |
|
Posts: 40 Rating:
|
Try to connect the transmitter 4-20mA direct to AI module, without any additional voltage serial to this signal. Best regards |